solarperson10
- San Diego, CA
- Designer
Hello everyone,
At many duplexes, there is a multimeter main outside with just two main breakers. Those breakers feed each unit that has a MLO main distribution subpanel somewhere in the home, usually garage. When we install solar on duplexes, we land the inverter's breaker on the main distribution subpanel. The 120% rule is met because the breaker and and busbar rating math works out (EX: 200A MLO Main distribution subpanel in garage, 200A main breaker at MSP, with 40A of solar)
My company always takes an extra step of adding a main breaker to the main distribution subpanel. The new main breaker in the subpanel is the same capacity as the main breaker outside. Noone can tell me where the code says that the main breaker has to physically be attached to the bus bar to meet the 120% requirements. I would argue that we can leave the subpanel MLO and use the main breaker outside for the 120% rule.
No one I work with can give me evidence (NEC or CALIFORNIA ELECTRICAL CODE) for why we are adding the breaker. I have seen other companies design keeping the main distribution sub MLO.
Thanks
Thanks