Hello all,
We have recently added another new pier to our marina, and have 5mA GFCI circuit breakers on all of the shore power pedestals on this pier. Article 555.3 reads
555.3 Ground Fault Protection. The main over current
protective device which feeds
the marina shall have ground
fault protection not exceeding
100mA. Ground fault protection
of each individual branch or
feeder circuit shall be permitted
as a suitable alternative.
We chose the latter, "Ground fault protection of each individual branch or feeder circuit shall be permitted as a suitable alternative." The pedestals came from Eaton, equipped with 5mA GFCI circuit breakers for each service. All works as it should, except when we get a boat equipped with one of many galvanic isolator monitoring systems. These boats trip the breakers immediately, the only way we have the ability to provide these customers is by moving them to the older docks without the new pedestals....or by disabling the galvanic isolator monitor which is not a viable nor reasonable option. It appears the isolator monitors send out a reference test on the line that trips the GFCI's.
Has anyone else experienced this, and what options do we have to resolve this short of putting these boats at the older piers that do not have the latest code wiring?
Thanks for any and all opinions, comments, or input.
We have recently added another new pier to our marina, and have 5mA GFCI circuit breakers on all of the shore power pedestals on this pier. Article 555.3 reads
555.3 Ground Fault Protection. The main over current
protective device which feeds
the marina shall have ground
fault protection not exceeding
100mA. Ground fault protection
of each individual branch or
feeder circuit shall be permitted
as a suitable alternative.
We chose the latter, "Ground fault protection of each individual branch or feeder circuit shall be permitted as a suitable alternative." The pedestals came from Eaton, equipped with 5mA GFCI circuit breakers for each service. All works as it should, except when we get a boat equipped with one of many galvanic isolator monitoring systems. These boats trip the breakers immediately, the only way we have the ability to provide these customers is by moving them to the older docks without the new pedestals....or by disabling the galvanic isolator monitor which is not a viable nor reasonable option. It appears the isolator monitors send out a reference test on the line that trips the GFCI's.
Has anyone else experienced this, and what options do we have to resolve this short of putting these boats at the older piers that do not have the latest code wiring?
Thanks for any and all opinions, comments, or input.