It is MCap. The bond wire is a #10 aluminum wire. You don't back wrap it, you are supposed to just cut it off.
wowHe's referring to the newer MCAP type MC cable which employs a bare #10 aluminum conductor in contact with the armor to form the EGC.
http://www.southwire.com/commercial/MCAPandHCFMCAP.htm
It makes me now think about regular AC cable. I thought the bonding strip was touching the armor already. Now the strip is just a bigger size?He's referring to the newer MCAP type MC cable which employs a bare #10 aluminum conductor in contact with the armor to form the EGC.
http://www.southwire.com/commercial/MCAPandHCFMCAP.htm
It makes me now think about regular AC cable. I thought the bonding strip was touching the armor already. Now the strip is just a bigger size?
He's referring to the newer MCAP type MC cable which employs a bare #10 aluminum conductor in contact with the armor to form the EGC.
http://www.southwire.com/commercial/MCAPandHCFMCAP.htm
If this is used in a box that will contain a receptacle, do you have to run a bonding jumper from the box up to the EGC terminal of the receptacle?
If the box is grounded then you would need either a bonding jumper or a self-grounding receptacle. Switches would not need a bonding jumper nor a self-grounding device. I believe that this MC cable used a larger bonding conductor when compared to AC cable (bonding tape/strip) because AC cable uses a stronger, thicker metal jacket. (At least is always seems that way when I cut it). :roll:
I really don't think you will find a connector that is not listed for grounding, so they all should be acceptable. They are all rated for both AC or MC cable, and many also for flexible metal conduit.I have been told that this cable needs a certain type of rotosplit tool to strip off the armor, and it might be worth mentioning that the fittings must be listed for the cable. I'm not sure if all MC fittings are listed for use with MCap.
Yes, that is a big reason for this design - the cable sheath is the EGC, and proper fittings must be used to provide continuity to the metal enclosures it terminates at.I guess I should have asked does the cable ground/bond the box?
I suppose, to answer my own question, if you have to cut the bare conductor off for it to fit in the connector, it would have to bond both the box and the receptacle.
UL approved for use with aluminum interlocking grounding metal clad cable, Type MCIA
(Southwire MCAP?)
MCAP? is a registered trademark of Southwire Company