New MCAP and HCFMC

Status
Not open for further replies.

tkb

Senior Member
Location
MA
Look in Electrical Contractor magazine, Sept 2005, page 147, top center.

Southwire has released their new MC and Health Care Facility MC that uses the jacket as a grounding path.

Instead of a green wire it has a #10 aluminum bare conductor between the mylar and the armor.

To terminate you would just cut off the aluminum ground wire.

I called Southwire and they said they are now shipping this product.

Last year I saw something on one of these sites about this new cable. It was called "MC Smart" or something like that.

South wire emailed me a couple of PDF cut sheets on these cables.

I don't know how to post them, but if anyone is interested and would like to post them I could forward them to you.

Tim
 

peter d

Senior Member
Location
New England
Re: New MCAP and HCFMC

Originally posted by tkb:
To terminate you would just cut off the aluminum ground wire.
I don't know if this would be a "ground wire", but a bond wire similar to AC cable. It serves no other purpose than to reduce the inductive reactance of the jacket. So how would this new cable be any different than AC cable?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: New MCAP and HCFMC

Tim

Instead of a green wire it has a #10 aluminum bare conductor between the mylar and the armor.
I think it must still have an insulated grounding conductor along with the 10 bare in order to provide redundant grounding for patient care areas.
 

tkb

Senior Member
Location
MA
Re: New MCAP and HCFMC

Yes on the HCFMC it has a green wire along with the jacket.

I described only the MC not the HCFMC.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: New MCAP and HCFMC

That makes sense. :cool:

I am not sure I understand what the new MC will be used for. :confused:

You know the jobs we work on often call for a copper EGC in each raceway, I doubt many engineers will back away from that just so we can use the new MC.

[ September 29, 2005, 07:23 PM: Message edited by: iwire ]
 

tkb

Senior Member
Location
MA
Re: New MCAP and HCFMC

The people that do design build will benefit from this the most I would say.

It is NEC compliant and UL listed.

[ September 29, 2005, 07:30 PM: Message edited by: tkb ]
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: New MCAP and HCFMC

The only deciding factor in picking this new HCFMC over HCFC will be the price difference between the two.

Roger
 