I am a registered architect by profession, I am looking for some advice concerning electrical distribution in my home woodworking shop. Hopefully my question will be welcome in this forum. Some background first. I have a shop with many 220 and 220 three phase pieces of equipment. I run my three phase equipment with a rotary phase converter rated at 10 hp. The shop is serviced with at double pole 30 amp circuit. This circuit does a fine job running the rotary phase converter and my 5 horsepower Tannewitz tablesaw. Ocassionally the tablesaw will trip the breaker which is run from my residential service. I could put a larger 40 amp breaker in the panel, but my service wire is a 10awg. As I have read on this forum the NEC recommends a 10 awg for 30 amp breaker as a maximum. The saw trips the breaker while starting up. I was told by several of my engineers that I might be able to try a HACR breaker. These I understand are used in the HVAC industry. Can I do this? Is this a "code worthy" application for my problem, or should I just run a new service to the shop say 50 amp and maybe a sub panel? I am glad to be a member here and hope this questions is fitting for this forum. Any help is appreciated.