new nec romex rules

Status
Not open for further replies.

fireryan

Senior Member
Location
Minnesota
I was a little confused with the new rules on romex. Can you no longer sleeve all your romex into a 2'' pvc then into the panel to make it look nice. And from what I understand you cant have more than 2 romex in the same hole in a stud? Am i understanding this right? Am i missing anything?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
This is the last paragraph of art. 334.80

Where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without maintaining spacing between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a).
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
fireryan said:
if i am reading this right i am getting the info on the wires in a bored hole in art 334.80

Art. 334.80 allows only 2 wires in a bored hole where thermal insulation, firecaulk, etc will be used-before you must derate.

I have never seen anyone caulk between the studs so that is usually not an issue.

If you put 4 12/2 nm cables in a hole you must derate for 8 current carrying conductors. Table 310.15(B)(2)(a) tells us we must derate 70% to 9 conductors. Since NM cable has 90 C conductors we can use the 30 amp rating from T310.15. 30 times 70% = 21 amps so you are still good. Add that 5 nm cable and you have to lower the ampacity of all the conductors to a 15 amp breaker
 

benaround

Senior Member
Location
Arizona
fireryan, Even though it's been done for years in some areas, sleeving all the

romex homeruns into the panel has never been code compliant. 334.30
 

Minuteman

Senior Member
benaround said:
fireryan, Even though it's been done for years in some areas, sleeving all the

romex homeruns into the panel has never been code compliant. 334.30

I'm not sure I follow you Frank. :confused:

334.30 ...Sections of cable protected from physical damage by raceway shall not be required to be secured within the raceway.
 

benaround

Senior Member
Location
Arizona
Minuteman said:
I'm not sure I follow you Frank. :confused:


That's probally a good thing you don't. Last I knew romex needed to be

supported at the panel by a romex connector, but, that was many,many years ago.

I didn't read 334.30 as ' those cables need physical protection ' as the cables

entering the panel. Hey, that's only twice this week I've been wrong.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
fireryan said:
So you must derate the ocpd when they are run together for longer than 24'' and you can still run in pvc

Yes, you can still run them in PVC but take a close look at the Article Pierre posted, 312.5(C). This installation method if very restrictive and it meet all seven conditions outlined in 312.5(C).
 

RUWired

Senior Member
Location
Pa.
Pertaining to 334.80, if a sleeve is used to protect the nm cables through the wood framing and fire stop sealant is used, derating does not apply?? If thermal insulation is used, derating does apply. The reason i say that is because, i am not in direct contact with the wood.

334.80 Ampacity.
Where more than two NM cables containing two or more current-carrying conductors are installed, without maintaining spacing between the cables, through the same opening in wood framing that is to be fire- or draft-stopped using thermal insulation, caulk, or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a) and the provisions of 310.15(A)(2), Exception, shall not apply.
Where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without maintaining spacing between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a).
 