I have a panel that has been installed, and its a 3phase 480v with a 250A main breaker.
I did a VA calculation of all the breakers that I'm going to be putting in it. I would like to know if I did this right.
4-60amp three pole breakers
3-50amp three pole breakers
2-20amp three pole breakers
so I use VA=(number of breakers)times(amps)times(80%)times(1.732)
(4)times(60amps)times(80%)times(1.732)=159,621.12VA
(3)times(50amps)times(80%)times(1.732)=99763.2VA
(2)times(20amps)times(80%)times(1.732)=26603.52VA
(159621.12VA)plus(99763.2VA)plus(26603.52VA)=285987.84VA
(285987.84VA)divided(480V)divided(1.732)=32amps
So does that mean that is have 32amps left over on the 250amp 3phase 480V main panel breaker?