fisherelectric
Senior Member
- Location
- Northern Va
New Ac has min circ ampacity of 30.4 amps. Old circuit is #8 Al SEC. If disconnect and breaker are rated @ 75 degrees can we use 75 degree column for XHHW and ampacity of 40 amps or must we use 60 degree column and ampacity of 30 amps, in which case we need a new circuit?
Inspector has already turned this down for not enough ampacity but I think he may be wrong. He also said the breaker was too big, a 40amp breaker, even though max breaker size per name plate is 50 amp max. I think he wrong.
Inspector has already turned this down for not enough ampacity but I think he may be wrong. He also said the breaker was too big, a 40amp breaker, even though max breaker size per name plate is 50 amp max. I think he wrong.