Hi guys.
A friend of mine is working with the county, the power company and several vendors to design and build a new RV park from the ground up and has asked me to advise on the electrical.
I have several questions.
First? Article 551 has some tables in it that detail what appears to be the absolute minimum for a park with 35 spaces. Table 551.73A indicates that the minimum demand factor for a 35 space park can be as low as %42. He intends to install UL listed manufactured electrical pedestals made by Midwest Industries. They are rated at 100 amps.
My question is, do we indeed have to install 100 amp breakers in the branch circuit distribution panel and connect it to 100 amp rated aluminum wire if we have all 35 pedestals include all three of the 20 amp 120 volt, 30 amp 120 volt and the 50 amp 120/240 volt receptacles? I ask because preliminary research has made it clear that the smaller tow behind RVs usually only have the 30 amp 120 volt power cords while the larger 5th wheel RVs usually have the 50 amp 120/240 volt power cords. As such it is more than unlikely that both the 30 amp and the 50 amp outlets will ever be used at the same time. Because he wants to have all three outlets available for his guests, if I calculate for both the 20 amp 120 volt outlet and the 50 amp 120 240 volt outlet, can I omit including the 30 amp 120 volt outlet in the demand factor calculation and supply for only the 50 and 20 amp outlets at 70 amps instead of 100 amps to save on the expense of the larger wire?
Thanks guys,
Norm
A friend of mine is working with the county, the power company and several vendors to design and build a new RV park from the ground up and has asked me to advise on the electrical.
I have several questions.
First? Article 551 has some tables in it that detail what appears to be the absolute minimum for a park with 35 spaces. Table 551.73A indicates that the minimum demand factor for a 35 space park can be as low as %42. He intends to install UL listed manufactured electrical pedestals made by Midwest Industries. They are rated at 100 amps.
My question is, do we indeed have to install 100 amp breakers in the branch circuit distribution panel and connect it to 100 amp rated aluminum wire if we have all 35 pedestals include all three of the 20 amp 120 volt, 30 amp 120 volt and the 50 amp 120/240 volt receptacles? I ask because preliminary research has made it clear that the smaller tow behind RVs usually only have the 30 amp 120 volt power cords while the larger 5th wheel RVs usually have the 50 amp 120/240 volt power cords. As such it is more than unlikely that both the 30 amp and the 50 amp outlets will ever be used at the same time. Because he wants to have all three outlets available for his guests, if I calculate for both the 20 amp 120 volt outlet and the 50 amp 120 240 volt outlet, can I omit including the 30 amp 120 volt outlet in the demand factor calculation and supply for only the 50 and 20 amp outlets at 70 amps instead of 100 amps to save on the expense of the larger wire?
Thanks guys,
Norm