Their is a new section in NEC 2017 section 250.94(B). Would anyone know what size conductor would be needed to bond the bus bar to service grounding electrodes?
I was of the opinion that it related to 250.64(D) where the same bus was allowed for GEC connections.
In large installations you are likely to have the 250.64 common GEC buss and 250.94(B) allows you to use that for communication.
(You might read the ROPs or ROCs to see the input from the CMP)
The code simply does not care what size bonding conductor is installed for that purpose and does not even require that grounding/bonding bar to be installed. It is a design issue and not a code issue and whatever the drawings show is fine.That would be possible for small space but in larger buildings like five to seven stories each with communications systems room multiple bus would be needed in each room and each room bus would need to be bonded to service ground bus. Those buses in communication room according to 250.94(B) are not only for communications systems but for other connections. that event bonding conductor that bonds the buses #4 or #6 awg would be too small
Found this
250.94 Bonding for Communication Systems.
In the 2017 NEC, two different methods are permitted for bonding communications systems.www.electricallicenserenewal.com