We are changing a 100 amp service to a 200 amp service with a new 200 amp breaker panel. I need to run a 2" pipe from the new panel to the existing part of the new house and take the wires from the 100 amp panel to a j-box. I will pull 20 20 amp circuts to the new j-box. How many grounds do I need to pull from the new panel to the j-box. Some of the old wiring has no ground.
 

iwire

Moderator
Staff member
Location
Massachusetts
Yes the derating will bite you in the rear, why not run a 100 amp feeder over to the old panel and just refeed it after separating the neutrals and grounds?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If I was faced with the same choices, #1 would be what Bob suggested: leave the existing panel as a sub-panel.

If I had to extend 20 20a circuits to a new panel, I'd gut the existing panel, use it as a J-box, and run 10 12/3's.

The direct answer to the original question is that the EGC need only be as large as required for the largest circuit.
 

220/221

Senior Member
Location
AZ
A) Install a sub panel

B) use romex/no pipe

C) Install 3, 3/4" conduits.

Whatever you do, install GFCI breakers for the ungrounded circuits. It will allow the use of grounded receps.
 