I am working on bring in new residential service to a property that is currently only on “OUTBACK non grid tied system”. The customer is not allowed to backfeed grid when new service is tied in. So I decided to use a transfer switch to ensure the solar/generator never back feeds the grid. The system is quite old and the inspector said it need to be rate Utility Interactive. Since I am not connecting the existing power system to the grid why would it need to be utility interactive?
The main service panel is located at the bottom of a hill approx 250ft away. I will take the service conductors up the hill and land them on source two. Then I will take the existing power and land it on source one and the load will be an upgraded service panel 200amp.
The main service panel is located at the bottom of a hill approx 250ft away. I will take the service conductors up the hill and land them on source two. Then I will take the existing power and land it on source one and the load will be an upgraded service panel 200amp.