The panel is purchased as a unit. It has to be rated Suitable for Use as Service Equipment (SUSE).
We can probably go back and forth on this all day and not get anywhere... :lol:
Typical "loadcenters" are purchased as a unit. Most other panelboards you get to select components that are added and basically either build your own or at least specify what is assembled before it is sent to you. It is possible to put together an assembly that has code issues, but the complete loadcenter is listed as it is for the most part, and sometimes you still can make field modifications that are in accordance with listing by adding or removing certain components. Some will be SUSE - but only if certain conditions are followed, take away (or add) the wrong component and you are in violation.
I do not believe it is the intent of the code to classify the buss in the former as a feeder, or the buss in the latter as a service conductor. One possible explanation could be that the bussing of a factory assembled and UL listed panelboard is not considered a conductor in the article 310 sense. Or maybe the definition just needs a little tweaking. Or, as is a common occurance in the code, when there is a specific article on something, it overrides the general rules so in the case of a panelboard we go to 408.
I dont follow you. Wouldn't "my reasoning" be that I DONT need the 125% for the inside panelboard? I guess I dont quite follow the thought experiment. Perhaps my belief that the panelboard is not a feeder explains it.
[/QUOTE]
Art 100 definitions:
Feeder.
All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device.
Conductor, Bare.
A conductor having no covering or electrical insulation whatsoever.
Conductor, Covered.
A conductor encased within material of composition or thickness that is not recognized by this Code as electrical insulation.
Conductor, Insulated.
A conductor encased within material of composition and thickness that is recognized by this Code as electrical insulation.
There is no definition of "conductor", so we go to common definitions of words from a dictionary. Wouldn't the panel bus be a conductor since it is not otherwise defined as anything else in the NEC? If the bus is a conductor - it is included in "all circuit conductors" in the definition of a feeder.
You can have in this order - circuit breaker - wire type conductor - panel bus - wire type conductor (supplied by subfeed lugs attached to opposite end of panel bus as the supply conductors) - second panel bus, and assume all mentioned components are rated for same current level.
Isn't the first panel bus part of the feeder circuit between the circuit breaker and the second panel bus? If not what do you call it? sure it is a panel bus but it is also a part of a feeder circuit.
Aren't branch breakers plugged on/bolted to the bus essentially feeder taps of very short length?