I need to run an UG service to upgrade an existing that is currently OH. The service will be 400 amp 120/208 three phase. I plan to install a 400 amp (320 continuos) meter socket on the side of the building and feed it underground. The meter will nipple into a 3R 400 amp MCB right next to it. From there it will go back underground a few feet into an adjacent electric shed where the existing service lives. Here i will install a 400 amp MLO panel to feed the four existing circuits that enter the building which is a restaurant.
I have gone over the job with the inspector and he is good with all of the above but I'm not sure of the right choices for conduits, wire, MCB or meter so please check my thinking.
One 3 inch PVC conduit sched 40 from the trench to the meter with an expansion coupling under the meter. 3 inch PVC nipple to the 3R MCB. One 3 inch PVC 40 back underground from the MCB to the MLO panel with an expansion coupling under the MCB enclosure.
The wire size to the meter and on to the MLO panel inside will be 400MCM CU with XHHW insulation for amperage of 380 amps at 90 degree. The connected load is around 200 amps and I'm thinking a 320 continuous is the right size for now and a little expansion later.
The available fault current from POCO on the new UG will be 15,000 amps. I will look for a MCB that exceeds 15KAIC. The rest of the breakers I assume can be 10KAIC?
I will extend the existing GEC with a compression connector and run it to the MCB.
Any suggestions are welcome. Thanks
I have gone over the job with the inspector and he is good with all of the above but I'm not sure of the right choices for conduits, wire, MCB or meter so please check my thinking.
One 3 inch PVC conduit sched 40 from the trench to the meter with an expansion coupling under the meter. 3 inch PVC nipple to the 3R MCB. One 3 inch PVC 40 back underground from the MCB to the MLO panel with an expansion coupling under the MCB enclosure.
The wire size to the meter and on to the MLO panel inside will be 400MCM CU with XHHW insulation for amperage of 380 amps at 90 degree. The connected load is around 200 amps and I'm thinking a 320 continuous is the right size for now and a little expansion later.
The available fault current from POCO on the new UG will be 15,000 amps. I will look for a MCB that exceeds 15KAIC. The rest of the breakers I assume can be 10KAIC?
I will extend the existing GEC with a compression connector and run it to the MCB.
Any suggestions are welcome. Thanks