aort11
Member
- Location
- United States
Right now I have a 200 amp service in a home. It goes from the transformer to meter via 3 wire 4/0. The meter is at the house, then to the main 200 amp disconnect in the panel. The goal is to do the following:
Ronk Model 7406MS (Meter base and transfer switch all in one)
2 x Siemens W0202MB1200CU (200 amp disconnect)
All 3 boxes mounted on a pole with the service coming from the pole to the meter. This is where I start to get confused. I know you are supposed to bond the N and G at your first disconnect, but would that be the transfer switch? It is not fused. I only have a 3 wire run to the home, so if I bond at the meter/xfer switch I'll need to add a ground to the home. The switch will also be feeding the 2 200 amp disconnects for detached buildings. The disconnects are there for Generator operation. There will be cable/communication lines from the buildings to the home. I know the two 200 amp disconnects should have the neutral and ground bonded with 4 wire feeding the buildings. My thought was to leave the home feed with 3 wire, unbonded N and G in the meter/xfer switch, Bonded at the main panel in home, then bond the N and G in each of the 200 amp disconnects before they feed the two other buildings with 4 wire.
Ronk Model 7406MS (Meter base and transfer switch all in one)
2 x Siemens W0202MB1200CU (200 amp disconnect)
All 3 boxes mounted on a pole with the service coming from the pole to the meter. This is where I start to get confused. I know you are supposed to bond the N and G at your first disconnect, but would that be the transfer switch? It is not fused. I only have a 3 wire run to the home, so if I bond at the meter/xfer switch I'll need to add a ground to the home. The switch will also be feeding the 2 200 amp disconnects for detached buildings. The disconnects are there for Generator operation. There will be cable/communication lines from the buildings to the home. I know the two 200 amp disconnects should have the neutral and ground bonded with 4 wire feeding the buildings. My thought was to leave the home feed with 3 wire, unbonded N and G in the meter/xfer switch, Bonded at the main panel in home, then bond the N and G in each of the 200 amp disconnects before they feed the two other buildings with 4 wire.