New Service to Feed the EV charges

Electriman

Senior Member
Location
TX
Hello every one,

A customer is adding a hand full of Fast EV chargers. Due to the amount of power that is required to feed the chargers, he either needs to get a new service or upgrade the existing service. But new service would be in conflict of NEC 230.3 (one service for each building). Therefore, he only can upgrade the existing service. Is there any exception applicable to this case to explain two services are permitted for this commercial customer?

Thank you in advance
 

retirede

Senior Member
Location
Illinois
Just add a service near the EVSE out in the parking lot.

Agreed. Good chance the utility will need to set a new transformer someplace anyway.

ETA - what are the voltages involved? The chargers will likely require 480V and depending on the existing business, it’s likely 208V. There is an exception to allow more than one service for different voltages.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Hello every one,

A customer is adding a hand full of Fast EV chargers. Due to the amount of power that is required to feed the chargers, he either needs to get a new service or upgrade the existing service. But new service would be in conflict of NEC 230.3 (one service for each building). Therefore, he only can upgrade the existing service. Is there any exception applicable to this case to explain two services are permitted for this commercial customer?

Thank you in advance
A second service can be added if it is for a different voltage/phase using the exception. If the existing service is a delta, or 120/208 wye, or single phase, a second service 277/480 wye can be added, unless they have changed the rules. The last time I done that was about 40 years ago, but do know of one in Chattanooga that was done 10 years ago.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
Hello every one,

A customer is adding a hand full of Fast EV chargers. Due to the amount of power that is required to feed the chargers, he either needs to get a new service or upgrade the existing service. But new service would be in conflict of NEC 230.3 (one service for each building). Therefore, he only can upgrade the existing service. Is there any exception applicable to this case to explain two services are permitted for this commercial customer?

Thank you in advance
A handful doesn't really help define what may be needed. Can you give quantity and ratings?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
230.2(C) has some allowances when a lot of power is needed. But as kingpb said we really need more details. I'm not even sure if 'fast' means Level II or Level III HVDC.
 

retirede

Senior Member
Location
Illinois
230.2(C) has some allowances when a lot of power is needed. But as kingpb said we really need more details. I'm not even sure if 'fast' means Level II or Level III HVDC.

The way I read the OP, he has already determined that the existing service is incapable of serving the new loads. He’s only questioning the legality of adding a second service.

While it’s not written in stone, “fast charging” is generally considered to be DC over 20KW.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
The way I read the OP, he has already determined that the existing service is incapable of serving the new loads. He’s only questioning the legality of adding a second service.
...
Those sections I cited still speak to whether a new service could be legal or whether upgrading the existing one is required.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Are those UL listed? 416Y/240V is a typical European voltage and is a 3-phase system. I think you could easily request a new 480V 3ph system then step it down to 416Y/240V.
Yeah, the poco’s hate oddball systems because they have to keep a spare in the yard, unless it’s pole mount where they can use a commonly used transformer.
 

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
This has been a two part question in my experience. It should be easy to satisfy the NEC by using one of reasons for an extra service listed in 230.2(B) and (C). The second is the POCO, they get to decide if they want to supply a second service. Most are okay for dedicated DCFC chargers if they will get a lot of use. They want to sell the energy.
 

Murphy79

Member
Location
Kansas City , MO
Occupation
Master Electrician/ Elelectrical Contractor/Instructor/ Solar
Hello every one,

A customer is adding a hand full of Fast EV chargers. Due to the amount of power that is required to feed the chargers, he either needs to get a new service or upgrade the existing service. But new service would be in conflict of NEC 230.3 (one service for each building). Therefore, he only can upgrade the existing service. Is there any exception applicable to this case to explain two services are permitted for this commercial customer?

Thank you in advance
I actually had to install (4) Tesla Level # chargers and it requires a seperated service for this application. It can be done. It also required me to build 1200a switchgear to accomodate.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
This has been a two part question in my experience. It should be easy to satisfy the NEC by using one of reasons for an extra service listed in 230.2(B) and (C). The second is the POCO, they get to decide if they want to supply a second service. Most are okay for dedicated DCFC chargers if they will get a lot of use. They want to sell the energy.
Many electric utilities no longer sell energy. They only provide the transmission capability. As a practical matter generally for residences they also do the billing for whomever is actually selling the energy and take responsibility for reading the meters and reporting usage to the energy supplier.
 

Knightryder12

Senior Member
Location
Clearwater, FL - USA
Occupation
Sr. Electrical Designer/Project Manager
I have never had a hard time getting a second service whether or not it was the same or different voltages. As long as it was "wink, wink" for a dedicated piece or pieces of equipment. Duke Energy (POCO) has never had a problem with it either.
 