Even with the separate enclosures it would look better if one found a way to not use that piece of SE cable feeding the far right disconnect.I see a lot of new houses with a meter base and separate disconnect. What are the options for this setup? I would think a combination meter with one or two built in disconnects would look better?
This, IMO, would be an improvement over what is pictured:
Or one panel on each side as we do it. Many people use the meter/main combo. It definitely is more compact and less labor intense but for some reason I still like the 2 panels for a 400 amp panel. Those 400 meter mains are about $600 - $700 dollars.
The pic of the service is an abortion imo.
I would do it as Dennis suggests or raise the 1st disconnect far enough to allow a raceway to run underneath it into the 2nd disconnect.Or one panel on each side as we do it.
Might that not be a line side breaker and a load side breaker? It's been mentioned in here that some utilities are now requiring a disconnect AHEAD of the meter socket.
Breaker probably not, unfused disconnect - many only want to see that on over 250 volts to ground if it is self contained metering, most popular place to see that is for 200 amp or less 480/277 volt services.I cannot even imagine our POCO requiring a breaker in front of their meter.
Breaker probably not, unfused disconnect - many only want to see that on over 250 volts to ground if it is self contained metering, most popular place to see that is for 200 amp or less 480/277 volt services.
Breaker probably not, unfused disconnect - many only want to see that on over 250 volts to ground if it is self contained metering, most popular place to see that is for 200 amp or less 480/277 volt services.
That scenario maybe.
120/240 service..... There are a lot of idiots out there that would love to be able to get in front of the meter with a well hidden tap.
Where our utility requires a disconnect ahead of their meter, they require that disconnect to contain the service OCPD.Breaker probably not, unfused disconnect - many only want to see that on over 250 volts to ground if it is self contained metering, most popular place to see that is for 200 amp or less 480/277 volt services.
1. Single, and three phase, 480V, less than 201 Amp, services
a) A breaker or fused disconnect located on the line side of the meter (cold sequence metering) is required for all 277/480V and 480V services 200 amp and below.
b) It shall be the customer’s responsibility to provide the proper interrupting rating device on the line side.
c) Ameren should be contacted to determine available short circuit current.
d) Use of separate enclosures for the line side protective device and the meter enclosure is acceptable. However they must be mounted directly above, or on a horizontal plane, within 4 feet of one another.
e) Continuous conduit with no LB’s or any other connector that could allow access to un−metered wiring is allowed between the protective device enclosure and meter enclosure.
f) Sealing provisions for the line side protective device must be provided to prevent access to un−metered conductors within this enclosure.
g) A pad lockable door for access by the customer to operate the protective device should be provided.
In my area I have not seen it for dwellings but some local power companies do require a disconnecting means of some type ahead of the metering for services greater than 250 volts to ground.