Hi,
We have a very old service transformer and switchboard (1950s) in one of our facilities with the following specs
ex. Transformer - 2500kVA - 13.2kV to 480V - 5.6% .
ex. Switchboard - 4000A - 480V - unknown kA rating
We are planning to replace these two just because they have reached or are close to there "end or cycle".
The new transformer is planned to match the specs the of the existing transformer and the new switchboard will be 65kA fully rated.
From the new switchboard we will be feeding couple of 400A air compressors which are about 300ft away.
Like all other piece of equipment here, these compressors are pretty old and don't have an SCCR rating.
The available short circuit current according to my calculation is about 15kA at the compressor panel with the new service.
i was wondering if someone can provide me with some insight on what are my options here? Can i just install these existing equipment with unknown SCCR to the new service? will this be a code violation?
if this would be a code violation, is changing out all the equipment with proper SCCR the best solution?
Any help would be appreciated.
Thanks
We have a very old service transformer and switchboard (1950s) in one of our facilities with the following specs
ex. Transformer - 2500kVA - 13.2kV to 480V - 5.6% .
ex. Switchboard - 4000A - 480V - unknown kA rating
We are planning to replace these two just because they have reached or are close to there "end or cycle".
The new transformer is planned to match the specs the of the existing transformer and the new switchboard will be 65kA fully rated.
From the new switchboard we will be feeding couple of 400A air compressors which are about 300ft away.
Like all other piece of equipment here, these compressors are pretty old and don't have an SCCR rating.
The available short circuit current according to my calculation is about 15kA at the compressor panel with the new service.
i was wondering if someone can provide me with some insight on what are my options here? Can i just install these existing equipment with unknown SCCR to the new service? will this be a code violation?
if this would be a code violation, is changing out all the equipment with proper SCCR the best solution?
Any help would be appreciated.
Thanks