On a pole mounted service with a 200amp breaker panel installed under the metercan ,I have seen several where a #6 bare grounding electrode conductor was stuck out of the meter can and split bolted to the poles #6 ground wire that the power co. installs on thier poles,,,,,is this an acceptable grounding electrode or should a ground rod be driven to supplement and bond to the power co. ground wire.Although this is a sufficient ground for the power co. high voltage I do not think this is an acceptable grounding electrode conductor for a service.Also,I always ground the neutral in the meter can and then extend an insulated ground wire down into the panel on its own bar,remove the jumper between the neutral bar and ground bar and install the bonding screw from the ground bar into the panel to bond the panel to ground and leave the neutral insulated from the ground in the panel,,,can the jumper between the ground bar and the neutral bar be left in place,seeing as how this is the main service entrance panel even though it is bonded in the meter can?