Hello all,
I have a question regarding bus sizing when installing new solar power systems. I do a lot of commercial electrical design, and I've found myself questioning whether I'm sizing AC panels correctly. Typically, we will install multiple inverters that feed back to a single AC panel. For example, we may install (3) 20KW inverters. These will all have their own separate runs back to an AC panel. I will size this new AC panel's main breaker based off the wattage of the inverters. This gives me a main breaker size of 100A (at 480V 3ph.). I would then run conduit from that 100A breaker back to a disconnect at the existing Main Switchboard, and then supply side interconnect the existing bus.
I have been sizing the new AC panel (with the 100A main circuit breaker with three inverter generators) bus at 200A. This is how I've been taught to do it, the theory being that the bus needs to be sized for backfeed from the utility. The idea is that if the utility is producing a load through that 100A main breaker and the inverters are also generating power, then hypothetically you could have more than 100A on that bus. Does this make sense? Or am I needlessly increasing the bus size of new AC panels?
This isn't really an issue at low wattage, but for bigger systems, I may have an 800 main circuit breaker with a 1600A bus. There's no way the utility will every provide 800A of power to a panel that's only connected to solar inverters, right? And the inverter output would be capped at 800A due to their individual breakers. Ultimately, I believe these AC panels should be rated off the main circuit breaker size (100A MCB = 100A bus, 800A MCB = 800A bus). I'm basically doubling the size of the bus to compensate for load flow from two different directions. Anyone have any opinions?
Let me know if you need clarification, this can be a little confusing to write out. Thank you.
I have a question regarding bus sizing when installing new solar power systems. I do a lot of commercial electrical design, and I've found myself questioning whether I'm sizing AC panels correctly. Typically, we will install multiple inverters that feed back to a single AC panel. For example, we may install (3) 20KW inverters. These will all have their own separate runs back to an AC panel. I will size this new AC panel's main breaker based off the wattage of the inverters. This gives me a main breaker size of 100A (at 480V 3ph.). I would then run conduit from that 100A breaker back to a disconnect at the existing Main Switchboard, and then supply side interconnect the existing bus.
I have been sizing the new AC panel (with the 100A main circuit breaker with three inverter generators) bus at 200A. This is how I've been taught to do it, the theory being that the bus needs to be sized for backfeed from the utility. The idea is that if the utility is producing a load through that 100A main breaker and the inverters are also generating power, then hypothetically you could have more than 100A on that bus. Does this make sense? Or am I needlessly increasing the bus size of new AC panels?
This isn't really an issue at low wattage, but for bigger systems, I may have an 800 main circuit breaker with a 1600A bus. There's no way the utility will every provide 800A of power to a panel that's only connected to solar inverters, right? And the inverter output would be capped at 800A due to their individual breakers. Ultimately, I believe these AC panels should be rated off the main circuit breaker size (100A MCB = 100A bus, 800A MCB = 800A bus). I'm basically doubling the size of the bus to compensate for load flow from two different directions. Anyone have any opinions?
Let me know if you need clarification, this can be a little confusing to write out. Thank you.