julian padilla
Member
- Location
- Houston, TX, USA
The size of a single-family dwelling is 25,117 square feet. The service is 120/240 volts single-phase. Without application of demand factors, what is the minimum number of general use, noncontinuous 120-volt, 15-ampere branch circuits?
1. 45
2. 32
3. 42
4. 14
See steps below:
Step_1: Table 220.12 lists 3VA/sq-ft. Calculate; 25,117 sq-ft x 3 VA/sq-ft = 75,352 VA. (Note: Lighting is considered a continuous load, however, do not apply this demand adjustment as stated for this specific question.)
Step_3: Calculate the power per circuit; P = I x E = 15 amperes x 120 volts = 1,800 VA / circuit.
Step_4: Calculate the number of 15 A circuits; Total Power / Power per Circuit = 75,352 VA / 1,800 VA = 41.86. Therefore, size up to 42 Circuits.
Do y'all agree that 42 circuits is the correct answer to this question?:?
1. 45
2. 32
3. 42
4. 14
See steps below:
Step_1: Table 220.12 lists 3VA/sq-ft. Calculate; 25,117 sq-ft x 3 VA/sq-ft = 75,352 VA. (Note: Lighting is considered a continuous load, however, do not apply this demand adjustment as stated for this specific question.)
Step_3: Calculate the power per circuit; P = I x E = 15 amperes x 120 volts = 1,800 VA / circuit.
Step_4: Calculate the number of 15 A circuits; Total Power / Power per Circuit = 75,352 VA / 1,800 VA = 41.86. Therefore, size up to 42 Circuits.
Do y'all agree that 42 circuits is the correct answer to this question?:?