Thanks for the Reply. So my question I'm asking is in regards to 110.16 Arc-Flash Hazard Warning, Other than Dwelling Units. It is real easy in Commercial installation where the equipment defined in the code as Service ends and Feeders or Branch Circuits begins. The code spells out that only services need the more detailed Arc-Flash Hazard Warning Labels with the detailed information that is required in NFPA 70E and in 2022 it said Feeders as well. Well the new code know states that only Feeders of over a 1000A. Then this code cycle a new definition was added Branch Circuit, Motor
Motor Branch Circuit) The circuit conductors, including equipment, between the motor branch-circuit short-circuit and ground-fault protective device and an individual motor. My interpretation on this new definition is that MCC's with individual bucket assemblies are by this definition NOT SERVICE equipment but branch circuits and only require the generic label that just warns qualified persons of the potential of the arc flash hazard. Even if people define these as Feeders I only have two Feeders over a 1000 amps most are 800 amps. I was just attempting to get a consensus of what Electrical Engineers with a PE would define this equipment. Of the ones I personally know they define MCC's as Feeders even then they are not over 1000A and need the more detailed Arc-Flash Label just the warning label. Thoughts