I have only been involved with NEC code issues for the last couple of years and I am learning new things every day. That said, I have come across a question that I am struggling to find the answer to, so here it is.
I am considering a design option for a PV system for a client. The system will be roughly 50kW DC and will be connected to an existing 208V 3-phase utility. To keep install costs down and utilize existing technology, we are proposing using 480V inverters, then knocking it down to the 208V for connection to the grid. The question I have is in regards to the transformer and protection thereof. I am curious if I would need disconnects on each side of the transformer. Per table 450.3(b), I am seeing a need for protection on the primary and the secondary side (we would be seeing more than 9A, so 125% of FL is applicable). I am really curious about putting in a fused D/S on each side of the transformer.
Thoughts?
I am considering a design option for a PV system for a client. The system will be roughly 50kW DC and will be connected to an existing 208V 3-phase utility. To keep install costs down and utilize existing technology, we are proposing using 480V inverters, then knocking it down to the 208V for connection to the grid. The question I have is in regards to the transformer and protection thereof. I am curious if I would need disconnects on each side of the transformer. Per table 450.3(b), I am seeing a need for protection on the primary and the secondary side (we would be seeing more than 9A, so 125% of FL is applicable). I am really curious about putting in a fused D/S on each side of the transformer.