Hello,
I am tasked with upgrading our equipment from starters to VFDs on a system. Also doing this process we are going to over size the VFD for future project to upsize a couple motors.
I have hit a brick wall trying to figure out how and why a Motor Feeder Disconnect OCPD was sized with this particular rating as well as how to size my new OCPD for this feeder if needed.
Current
We have 600 AMP Time delay Fuses used as OCPD for the feeder. This Feeder feeds
(9) 50 HP Motors FLC per table 430.250 = 65A With Motor Branch circuit short circuit/Ground fault protection =100A MCCB each
(3) 10HP Motor FLC per table 430.250 = 14A With Motor Branch circuit short circuit/Ground fault protection =50A MCCB each
(3) 1.5HP Motor FLC per table 430.250 = 3A With Motor Branch circuit short circuit/Ground fault protection =7A MCCB each
(12) 20kW Heaters = 24A per calcs With Motor Branch circuit short circuit/Ground fault protection =30A MCCB each
First question, Should the original Feeder OCPD have a rating of 125%*100A MCCB+8*65A FLC+3*14A FLC+3*3A FLC +12*24A = 984 or 1000A???? per 430.62
I do not understand where we came up with 600A Fuses?
My second question is really dependent on if I am correct with my thinking in the first question.
I am replacing(6) of the across the line starters with VFDs which documentation states input 140A recommended OCPD 200A rating.
Should my Feeder OCPD = 1.25*200+5*140+3*65+3*14+3*3+12*24 = 1484 or 1500A??
Does it matter if we will have 3 separate panels with a 400AMP breaker feeding (1) VFD, (1) 50HP, (1)10Hp, (1)1.5HP and (4)20kW heaters
and 3 separate panels with a 200Amp Breaker feeding (3) VFDs each?
Any help and understanding is much appreciated. Thank you.
I am tasked with upgrading our equipment from starters to VFDs on a system. Also doing this process we are going to over size the VFD for future project to upsize a couple motors.
I have hit a brick wall trying to figure out how and why a Motor Feeder Disconnect OCPD was sized with this particular rating as well as how to size my new OCPD for this feeder if needed.
Current
We have 600 AMP Time delay Fuses used as OCPD for the feeder. This Feeder feeds
(9) 50 HP Motors FLC per table 430.250 = 65A With Motor Branch circuit short circuit/Ground fault protection =100A MCCB each
(3) 10HP Motor FLC per table 430.250 = 14A With Motor Branch circuit short circuit/Ground fault protection =50A MCCB each
(3) 1.5HP Motor FLC per table 430.250 = 3A With Motor Branch circuit short circuit/Ground fault protection =7A MCCB each
(12) 20kW Heaters = 24A per calcs With Motor Branch circuit short circuit/Ground fault protection =30A MCCB each
First question, Should the original Feeder OCPD have a rating of 125%*100A MCCB+8*65A FLC+3*14A FLC+3*3A FLC +12*24A = 984 or 1000A???? per 430.62
I do not understand where we came up with 600A Fuses?
My second question is really dependent on if I am correct with my thinking in the first question.
I am replacing(6) of the across the line starters with VFDs which documentation states input 140A recommended OCPD 200A rating.
Should my Feeder OCPD = 1.25*200+5*140+3*65+3*14+3*3+12*24 = 1484 or 1500A??
Does it matter if we will have 3 separate panels with a 400AMP breaker feeding (1) VFD, (1) 50HP, (1)10Hp, (1)1.5HP and (4)20kW heaters
and 3 separate panels with a 200Amp Breaker feeding (3) VFDs each?
Any help and understanding is much appreciated. Thank you.