noon9elec
Member
- Location
- Bourne, MA
- Occupation
- Self employed Electrical Contractor
So its been awhile since I have done any type residential work, as my work over the last 3 years involves service only. No matter, but I am replacing an underground service 500 ft. long. While there is no significant load, I was thinking that a typical 4/0 URD, without reduced neutral would satisfy everyone. I was planning on a 200-amp panel, and I researched the 4/0 URD-rated for 308 amps. thats pretty much what was there before, I shouldn't have a problem, correct? Thanks