New XFMR and Panel in existing facility

Status
Not open for further replies.

Bachmayer

New User
Location
Ennis, TX
Occupation
Journeyman Electrician
Contracted electricians installed a new 3ph, transformer and new panel in our existing building. They put the high leg on the"C" phase instead of the"B" phase. Is this acceptable according to 408.3(E)(1)? It is supplying power only to one room in the existing building.
 
IMO, it's a violation of the Section you quoted,.
also note 408.36(F)(1)
 