You would connect one side of each coil together to form a center point. This would be your neutral. I would look like the WYE version of this:

t-f21.gif
 
Does it matter which way the winding is connected?
If a winding is connected in reverse will there be a problem.

Let's say the delta is connected
H1 on winding 1 to H2 on winding 2
H1 on winding 2 to H2 on winding 3
H1 on winding 2 to H2 on winding 1

X1 on all windings are the phases
X2 connect together in the center of the wye

What would happen if one winding was connected backwards?
 
What would happen if one winding was connected backwards?

If one of the secondary windings is connected backwards, then the output phase angles and line-line voltages will be wrong. In what is supposed to be a 480/277 system, all of the phase-neutral voltages would still be 277V, and one of the phase-phase voltages would still be 480V, but the other two phase-phase voltages would be 277V. Additionally, neutral current would not balance.

If one of the primary windings is connected backward in a bank of separate single phase transformers, you would have the same result.

If one of the primary windings is connected backward in a three phase transformer with a common core, then in addition to the above problems, the core magnetization will be wrong.

-Jon
 
Does it matter which way the winding is connected?
If a winding is connected in reverse will there be a problem.

Let's say the delta is connected
H1 on winding 1 to H2 on winding 2
H1 on winding 2 to H2 on winding 3
H1 on winding 2 to H2 on winding 1

X1 on all windings are the phases
X2 connect together in the center of the wye

What would happen if one winding was connected backwards?

it'll smoke.
 
I knew that there would be a problem, but I wanted to get it out there for the OP.
 
Follow-up question.
What is the lowdown if there are 3- 112.5 kva pole mounted transformers, at some undefined primary voltage, for the electric service? What is the total secondary current, if the secondary voltage is 277/480v Y? I'm confused as to how this differs from 1- 112.5 kva 3 phase transformer.
Thanks for the help.
 
In a wye configuration, the current in the coil is the same as the current in the conductor that attaches to the transformer. Therefore, the output current of a 480 volt wye is the same as the output current of a 277 volt coil. :smile:
 