J JoeNorm Senior Member Location WA Jun 16, 2020 #1 I am running 6/2 NM wire good to 55 amps. With a continuous duty factor my load is 52 amps. I am allowed to put this on a 60 amp breaker, correct?
I am running 6/2 NM wire good to 55 amps. With a continuous duty factor my load is 52 amps. I am allowed to put this on a 60 amp breaker, correct?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 16, 2020 #2 Yes, the next size up rule in 240.4(B) would allow the 60 amp OCPD on a 55 amp conductor.