Hi
I am supplying a 120' away sub panel l thru a set of #6 thhn, cu in an apartment building.

Question is,
can use 70A ocpd for the feeder main ; according to next-larger size rule ?????

Also,
70A ocpd for the feeder main; What size copper wires can be used to feed that apartment sub panel. ???????

Thank you
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
215.2 requires that your feeder conductor have the amapcity to supply the load so your #6 THHN would be good for a 65 amp loadassuming 75° terminations. If your load does not exceed 65 amps, you are good with a 70 amp overcurrent device.
 

kwired

Electron manager
Location
NE Nebraska
215.2 requires that your feeder conductor have the amapcity to supply the load so your #6 THHN would be good for a 65 amp loadassuming 75° terminations. If your load does not exceed 65 amps, you are good with a 70 amp overcurrent device.
I second that and add that if your feeder is NM cable - you are limited to 60C ampacity.
 