Got a test question that I'm not agreeing with but now I'm questioning it. Here it is:
"What is the MAX standard size OCPD that may be used to protect a 4/0 THWN conductor that is not serving a motor load?"
Seems simple enough. The ampacity of 4/0 THWN is 230A. There are many loads that are continuous that are not motors so I add the 125% for a possible continuous load which brings it to 287.5A. Nothing stated says it doesn't meet the requirements of 240.4b so next size up is 300A. The answer they have is 250A which implies they used the next size up rule but did not apply the continuous. So my question is, Does the 125% continuous load increase negate the next size up rule?
"What is the MAX standard size OCPD that may be used to protect a 4/0 THWN conductor that is not serving a motor load?"
Seems simple enough. The ampacity of 4/0 THWN is 230A. There are many loads that are continuous that are not motors so I add the 125% for a possible continuous load which brings it to 287.5A. Nothing stated says it doesn't meet the requirements of 240.4b so next size up is 300A. The answer they have is 250A which implies they used the next size up rule but did not apply the continuous. So my question is, Does the 125% continuous load increase negate the next size up rule?