240.4 allow one to use the "next size up" rule for feeders up to and including 800A. 240.21(C) says that one MAY NOT apply this rule on transformer secondaries.
What does the code say about service entrance conductors. i.e. I'm specifying an 800A service (happens to be 208Y/120V if that matters). So in this case, I'm on the secondary side of utility owned pad mounted transformer which will be whatever size they deem appropriate. May I apply the 240.4, next size up rule and therefore use 2 sets of 500kcmil with a nominal rating of 760A with an 800A service disconnect at the building OR must I use 2 sets of 600kcmil such that the ampacity in keeping with 240.21(C) of my feeder matches (in this case exceeds) the 800A service disconnect?
Thanks,
Mike
What does the code say about service entrance conductors. i.e. I'm specifying an 800A service (happens to be 208Y/120V if that matters). So in this case, I'm on the secondary side of utility owned pad mounted transformer which will be whatever size they deem appropriate. May I apply the 240.4, next size up rule and therefore use 2 sets of 500kcmil with a nominal rating of 760A with an 800A service disconnect at the building OR must I use 2 sets of 600kcmil such that the ampacity in keeping with 240.21(C) of my feeder matches (in this case exceeds) the 800A service disconnect?