Running three #4 THHN w #8 ground from 200A main to 100A sub in detached garage.
Since #4 THHN is 95A @90, can we put 100A breaker in main panel as OCPD for the Garage sub?
That said, 100A garage sub panel will also have a car charger. So that particular EV branch circuit must be protected (as i understand) at 125% of the of the #4 THHN feeding the garage sub. So that means max EV breaker size 76A — would have to have 70A since no one makes a 75 or 76, right?
Thanks!