I have read the current threads related and still have issues.
1. If the lights come on during occupancy, even with ASHRAE 90.1 50% max level settings, why does the FA have anything to do with power outage to lighting.
Just do not use Vacancy manual ON feature for pathways.
2. Why are they reducing the possible light output if power is available by tripping the power branch circuit to the lights. Most EM drivers are only placed to meet the minimum egress levels upon power outage. If you still have power then the higher level possible is puposely reduced for no reason.
3. In some buildings the Fire Alarm testing takes more than 90 minutes, thus the EM drivers will be spent and not be available if needed shortly after.
4. Add daylight sensors and digital dimming on fixtures. If not then schedule building OFF will not have the devices to force the lights ON without going to each room and bypassing the manual switches. These devices are one more point of failure and adds to the Fire Alarm costs.
5. For DoD projects ASHRAE 90-1 is LAW. NFPA is the safety Codes, ICC is only building classifications.
Question: I cannot get NFPA to respond to this. I cannot find American made products (requirement for most DoD projects). Does anybody have this backup justification from NFPA? Especially since there is a much simpler way of doing this and meet the requirements before this line was added.
1. If the lights come on during occupancy, even with ASHRAE 90.1 50% max level settings, why does the FA have anything to do with power outage to lighting.
Just do not use Vacancy manual ON feature for pathways.
2. Why are they reducing the possible light output if power is available by tripping the power branch circuit to the lights. Most EM drivers are only placed to meet the minimum egress levels upon power outage. If you still have power then the higher level possible is puposely reduced for no reason.
3. In some buildings the Fire Alarm testing takes more than 90 minutes, thus the EM drivers will be spent and not be available if needed shortly after.
4. Add daylight sensors and digital dimming on fixtures. If not then schedule building OFF will not have the devices to force the lights ON without going to each room and bypassing the manual switches. These devices are one more point of failure and adds to the Fire Alarm costs.
5. For DoD projects ASHRAE 90-1 is LAW. NFPA is the safety Codes, ICC is only building classifications.
Question: I cannot get NFPA to respond to this. I cannot find American made products (requirement for most DoD projects). Does anybody have this backup justification from NFPA? Especially since there is a much simpler way of doing this and meet the requirements before this line was added.