Does NFPA 110 (2005) address (optional) Standby Generator Systems? It doesn't appear to have any standby system requirements...
NFPA 110 is called Standard for Emergency and Standby power systems.
The scope (1.1) says it covers performance requirements for emergency and standby power systems.
Then it says (1.1.2) the standard covers installation, maintenance, ? as they pertain to the performance of the emergency power supply system (EPSS).
(1.2) says the purpose contains performance requirements for an EPSS.
The definition of EPSS is Emergency Power Supply System.
They don't define Standby Power Supply System (I know the NEC does).
It appears the entire document (except the name of the document and scope) is regarding Emergency Systems (not standby systems).
Does this code (NFPA 110) consider standby systems an EPSS for the purpose of this document? This doesn't seem to make sense because of the different requirements for emergency vs. standby systems.
I have a generator permit rejection saying they want to see compliance with NFPA 110 (the class and level of the generator, adequate heating, cooling and ventilating, etc?) but this all appears to all be in regards to emergency systems, not optional standby systems.
I have a 400KW genset outside in a sound/weather enclosure on a 500gal subbase fuel tank.
Please help. Thanks in advance!!