What are the differences (Definitions) between an Emergency Generator and a Stand-by Generator? NFPA refers to Level 1 and level 2 but I can find where it defines Emergency and Stand-by.
Is level I Emergency and Level 2 Stand-by or is there still another classification?
This I know :
4.4* Level.
This standard recognizes two levels of equipment installation, performance, and maintenance.
4.4.1* Level 1 systems shall be installed when failure of the equipment to perform could result in loss of human life or serious injuries.
4.4.2* Level 2 systems shall be installed when failure of the EPSS to perform is less critical to human life and safety and where the authority having jurisdiction shall permit a higher degree of flexibility than that provided by a Level 1 system.
4.4.3 All equipment shall be permanently installed.
Jim
Is level I Emergency and Level 2 Stand-by or is there still another classification?
This I know :
4.4* Level.
This standard recognizes two levels of equipment installation, performance, and maintenance.
4.4.1* Level 1 systems shall be installed when failure of the equipment to perform could result in loss of human life or serious injuries.
4.4.2* Level 2 systems shall be installed when failure of the EPSS to perform is less critical to human life and safety and where the authority having jurisdiction shall permit a higher degree of flexibility than that provided by a Level 1 system.
4.4.3 All equipment shall be permanently installed.