NFPA 20 says for fire pump 10.4.3.3.1 "The circuit breaker shall have the following electrical characteristics:
(I) A continuous current rating not less than 115 percent of the rated full-load current of the motor"
However NEC 2014 Article 695.4(B)(2)(a)(1) which says to size per 6x FLA= LRC or 695.4(B)(2)(a)(2) assembly listed for fire pump.
Am I missing something. Is their a difference between two? Why is their discrapency?