A question. Does anyone know of a hazardous vapor detection system compliant with NFPA 37 Section 4.1.2.2.3 (2015)? Does anyone know a manufacturer that would have this type of system under their line of products?? I want to tie the hazardous vapor detection to an exhaust fan in a detached generator building, based on the amount of hazardous vapors present. I don't have any experience with these types of systems.
4.1.2.2.3* Dedicated detached structures shall have ventilation designed to prevent a hazardous accumulation of flammable vapors or gases, both when the engine is operating and when it is shut down.
A.4.1.2.2.3 Explosion venting for a fuel explosion should be considered for large engine installations. In some installations where it might not be practical for the normal constantly operating ventilation to prevent the accumulation of flammable vapors or gases from leakage, a hazardous vapor detection system can be installed. The system is often set up to detect the hazardous vapors at two concentration levels (percentage of the lower explosive limit, LEL).
If the first (lower) level is reached, the ventilation volume is increased by use of a purge fan to remove the vapors. If the second (higher) level is reached, the operation is shut down and the enclosure inverted as the ventilation is stopped. The inverting is normally done quickly and maintained until the leak is stopped, after which the entire hazard volume is purged while operations are resumed.
4.1.2.2.3* Dedicated detached structures shall have ventilation designed to prevent a hazardous accumulation of flammable vapors or gases, both when the engine is operating and when it is shut down.
A.4.1.2.2.3 Explosion venting for a fuel explosion should be considered for large engine installations. In some installations where it might not be practical for the normal constantly operating ventilation to prevent the accumulation of flammable vapors or gases from leakage, a hazardous vapor detection system can be installed. The system is often set up to detect the hazardous vapors at two concentration levels (percentage of the lower explosive limit, LEL).
If the first (lower) level is reached, the ventilation volume is increased by use of a purge fan to remove the vapors. If the second (higher) level is reached, the operation is shut down and the enclosure inverted as the ventilation is stopped. The inverting is normally done quickly and maintained until the leak is stopped, after which the entire hazard volume is purged while operations are resumed.