Trying to close out a project where the GC's HVAC subcontractor has meet the 0.1 inches of water between interior walls of (2) MCC rooms and (1) Control room. I've read threads on this site discussing ventilation but nothing regarding the outward velocity of 60 ft/min. Installed in each of these rooms is an air handling unit for heat and cool with a fresh air inlet to each unit. I may be knocking at the wrong house but I thought I would pose the following question anyway. If anyone of these units is at it's peak performance, will it be able to supply the required outward velocity of 60 ft/min without a stand alone pressurization system and all the doors are open? This is neglecting leakage through wall penetrations, gaps in conduit sealant, etc..