NFPA 70E Arc Flash Boundries

Status
Not open for further replies.

mjc1060

Senior Member
Does 70E require arc flash boundries marked on the floor. That is are the boundries marked with something like yellow(caution) paint. Before any work begins are the boundries are physically visible.
 

mayanees

Senior Member
Location
Westminster, MD
Occupation
Electrical Engineer and Master Electrician
No...

No...

The arc flash boundary alerting requirement is met by it being displayed on the AF label.
It's a good idea, IMO, to use additional techniques to identify the boundary, but along with that then there would need to be sitewide training so everyone could know what's being done (i.e. red/yellow/orange paint for AFB)
John M
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Does 70E require arc flash boundries marked on the floor. That is are the boundries marked with something like yellow(caution) paint. Before any work begins are the boundries are physically visible.

There is no need to mark the floor, just as there is no need to permanently mark working clearances. The AF boundary only exists when someone is "interacting in a manner that would cause an arc" not just simple interaction.

Many Electrical Safe Work Practices programs require the use of 'caution tape' or other portable/temporary barricades.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
what if electrical panels are in an employee break room. how much room has to be between the panels and a lunch table ?
None, other than the NEC standard clear space.
The arc flash boundary only applies when there is 'interaction that can cause an arc'.
 

al

Senior Member
Location
Minnesota
Interaction

Interaction

There is no need to mark the floor, just as there is no need to permanently mark working clearances. The AF boundary only exists when someone is "interacting in a manner that would cause an arc" not just simple interaction.

Many Electrical Safe Work Practices programs require the use of 'caution tape' or other portable/temporary barricades.

How would you define a simple interaction verses an interaction that would cause an arc?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
NFPA70E is fraught with what needs to be done but, purposely, there is not much detail on how to accomplish it.

See the NFPA70E definition of Arc Flash Hazard.
Informational Note #1 says normal operation is normally not an issue, Note #2 is the reference for Zog's posting directing you to the task tables.

But then to make things clearer (?), the committee added Note #2 to 130.7(A), which effectively says; in the experience of the [NFPA70E] committee members normal operation of properly maintained enclosed equipment <600V is not likely a hazard.

So there is no single correct answer, but, statistically it is worse to be operating equipment, than it is walking past or simply sitting in the same room with it.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
No. Only the equipment itself must be labeled, and only for when the incindent energy is larger than 1.2 cal/cm sq. (see attached NFPA 130.5(C)

130.5(C) makes absolutely no mention of an incident energy level cut off /exclusion. If you are going to examine, service, adjust, or maintain it, while energized, it needs to be labeled.
 

kenaslan

Senior Member
Location
Billings MT
See 3rd line down in blue, The above was taken from the NFPA 70E Handbook.

"Only the equipment where the incident energy level is greater than 1.2 cal/cm2 needs to be marked, but that decision depends on a facility?s safety program."
 

kenaslan

Senior Member
Location
Billings MT
It is the third line down in the blue section.

130(A) Arc Flash Boundary. The arc flash boundary for systems 50 volts and greater shall be
the distance at which the incident energy equals 5 J/cm2 (1.2 cal/cm2).


"The arc flash boundary is the boundary determined either through calculation or through the
use of Table 130.7(C)(15); it separates an area in which a person is potentially exposed to a
second-degree burn injury from an area in which the potential for injury does not include a
second-degree burn. All body parts closer to an arc flash hazard than the arc flash boundary
must be protected from the potential thermal effects of the hazard. The arc flash boundary is
established at the point where the amount of incident energy that an employee could be exposed
to is 1.2 cal/cm2 or greater. If the incident energy is less than 1.2 cal/cm2, burns could
occur, but they will not be second-degree or worse."

energy less than 1.2 cal/cm2 need not be addressed
 

kenaslan

Senior Member
Location
Billings MT
I would respectfully disagree. True it is not part of the original text, it is an explanation endorsed by the NFPA, written by the NFPA. Also 130(A) states ?Arc Flash Boundary. The arc flash boundary for systems 50 volts and greater shall be
the distance at which the incident energy equals 5 J/cm2 (1.2 cal/cm2).?, hence no labeling requirement exist for under 1.2 cal/cm2 as the boundary itself is 1.2 cal/cm2.

On a side note, I print arc flash labels daily for many engineering firms and have yet to print any with a level of under 1.2

Time for the weekend my Harley is calling out my name.
 

the blur

Senior Member
Location
cyberspace
I'm in my kids elementry school, and the panel(s) are in the hallway. it's locked, but they obviously work on it at times. how do they draw the boundry ? close the hallway ?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
True it is not part of the original text, it is an explanation endorsed by the NFPA, written by the NFPA.

Yes you may disagree.

The blue text is not'endorsed nor witten by the NFPA, it is simply someones opninon that the NFPA publishes.

I have printed and installed thousands of labels on equipment where the incident energy is less than 1.2 cal/cm?.
 