There is some confusion in the workplace about the tables 130.7(C)(9). We have clearly marked labels in some areas above catagory 4 up to 100+ Cal/CM2. Other areas lower. Some people feel that these labels can be overruled by this table. Example: 600 V Class switchgear. Voltage testing. Listed as 2*. Tell me why this isn't above a catagory 4 if the sticker says above catagory 4? Thanks.
Did you do an arc flash analysis/ hazard risk study? If so, then you CANNOT use the tables, as Jim mentioned.
Actually, now that I think about it, if you do a study and then determine that the calculated cal/cm2 is lower than what the ratings are for the task tables, then I think that you can still use the task tables. I might be wrong about this. I don't have a copy of the 70E in front of me. If I am wrong about this, I hope someone else chimes in with a correction.
But here's the catch-22 of it all. You can't just outright say "we are going to use the task tables" because in order to use the task tables, you need to determine (i.e. a mini-analysis) whether or not you even qualify to use the tables. If you don't qualify to use the task tables, then you have to do the analysis/study. IMHO, you would be better off with just doing the analysis/study and be done with it.
My own personal opinion is that the task tables be done away with. I have my reasons for it.