NFPA 70E PPE table for work 240V and below
Natfuelbilll
Does anyone have a arc flash study that would support the "voltage testing" task of Hazard risk category 1, while working on the load end of a branch circuit fed from a 120/240V panelboard?
I know of no calculation method for determining incident energy of an arc flash on a single phase circuit. My recommendation is to use the "task table" in NFPA70E.
Panelboards or Switchboards rated >240 V and up to 600 V
(with molded case or insulated circuit breakers) ? Notes 1
And 3
Work on energized parts, including voltage testing
Hazard/Risk V-rated V-rated Tools
2* Gloves
YES
The nature of my question is if at the end of a 10' length of say #12 copper, fed from any MVA source, if the Hazard Risk Category is still up there requiring 2*.
IEEE has no formula to confirm your "hunch".
The present NFPA 70E task tables have an exception for 240V maximum situations where the fault current is less than 10kA. And, it is possible to calculate single phase fault currents.
Actually, IEEE does have their IEEE-1584 and NFPA 70E.
My question is more directed to anybody who has used Arc Flash software, or has results of a study, at the end of a branch circuit.
I use arc flash software regularly. I know of no method to give you the answer you want.
Neither IEEE 1584 nor NFPA 70E have any formulae to calculate arc flash incident energy for single phase circuits. If you can not calculate the energy, your only choice is to use the task tables.
Nat -
Just curious. It's only one calculation, why don't you just do it by hand using the formulas from 1584 or 70E?
carl