Under Table 130.7(C)(9)(A) in the NFPA 70E 2004 in working on energized parts on panelboards from 240V to 600V it states "hazard risk category 2*"
In the notes it states a double layer switching hood must be used. I beleive that a double layer hood would put you into category 3.
Am I right to assume that this is because the Table 130 is just an estimated guideline for certain tasks and therefore may be subject to over protection?
If so in order to get a more accurate level of protection an arc flash analysis should be performed?
Terry Smeader
(edited to remove url)
[ December 28, 2005, 06:43 AM: Message edited by: don_resqcapt19 ]
In the notes it states a double layer switching hood must be used. I beleive that a double layer hood would put you into category 3.
Am I right to assume that this is because the Table 130 is just an estimated guideline for certain tasks and therefore may be subject to over protection?
If so in order to get a more accurate level of protection an arc flash analysis should be performed?
Terry Smeader
(edited to remove url)
[ December 28, 2005, 06:43 AM: Message edited by: don_resqcapt19 ]