This question is more NFPA 72/110 than NEC but I will ask here anyway.
NFPA 72 allows battery backup to be sized for 4 hours if the secondary power supply (generator) meets NFPA 110 requirements for a type 10, Class 24, Level 1 system.
Although the section only mentions the generator, is it correct that the distribution between the generator and FACP needs to be designed as emergency power? Site we are working at has generators that would meet the NFPA 110 requirement but there is no segregation of 700/701/702 loads. (all are 702 I guess). I am assuming I need 24 hour battery for our FACP, but want to make sure I understand correctly.
NFPA 72 allows battery backup to be sized for 4 hours if the secondary power supply (generator) meets NFPA 110 requirements for a type 10, Class 24, Level 1 system.
Although the section only mentions the generator, is it correct that the distribution between the generator and FACP needs to be designed as emergency power? Site we are working at has generators that would meet the NFPA 110 requirement but there is no segregation of 700/701/702 loads. (all are 702 I guess). I am assuming I need 24 hour battery for our FACP, but want to make sure I understand correctly.