EC friend calls me, failed final on a residential project few towns over. Said he couldn't have a smoke detector within 36" of an HVAC return. Hallway is too small to give 36" clearance anyway. Asked for advice .....
Inspector sent this.....
17.7.4 Heating, Ventilating, and Air-Conditioning (HVAC).
17.7.4.1* In spaces served by air-handling systems, detectors
shall not be located where airflow prevents operation of the
detectors.
I sent this....
17.1.5
The requirements of single- and multiple station alarms and household fire alarm systems shall be determined in accordance with Chapter 29.
29.11.3.4 Specific Location Requirements. The installation of smoke alarms and smoke detectors shall comply with the following requirements:
(8) Smoke Alarms and smoke detectors shall not be installed within a 36 in. (910 mm) horizontal path from the supply registers of a forced air heating or cooling system and shall be installed outside of the direct airflow from those registers.
This is the inspectors reply....
I forwarded it to the state construction codes dept; probably take a few days to hear back, but wanted another opinion on the 17.1.5; I'm interpreting that correctly, right? Chapter 17 isn't applicable to residential?
Inspector sent this.....
17.7.4 Heating, Ventilating, and Air-Conditioning (HVAC).
17.7.4.1* In spaces served by air-handling systems, detectors
shall not be located where airflow prevents operation of the
detectors.
I sent this....
17.1.5
The requirements of single- and multiple station alarms and household fire alarm systems shall be determined in accordance with Chapter 29.
29.11.3.4 Specific Location Requirements. The installation of smoke alarms and smoke detectors shall comply with the following requirements:
(8) Smoke Alarms and smoke detectors shall not be installed within a 36 in. (910 mm) horizontal path from the supply registers of a forced air heating or cooling system and shall be installed outside of the direct airflow from those registers.
This is the inspectors reply....
We looked over all the material and we are going to keep it as a requirement. I do appreciate your help on it.
I forwarded it to the state construction codes dept; probably take a few days to hear back, but wanted another opinion on the 17.1.5; I'm interpreting that correctly, right? Chapter 17 isn't applicable to residential?