SD Dylan
Member
- Location
- Franklinville, NJ
I'm working on selecting cables for general 24V signals and I'm stuck determining what requirements makes sense and what is actually correct.
Issues 1: AWM
For the most part, AWM isn't accepted in NFPA 79 for most applications. But I found this:
12.9.2 Appliance wiring material (AWM) shall be permitted under any of the following conditions.
12.9.2(1) Where part of an assembly that has been identified for the indented use
So if a website says their 3 conductor cables with molded ends are intended for sensors and valves are they ok to use? Are there other UL ratings that still need to be met?
Issue 2: Cable routing and rating requirements
If I'm selecting a multi-conductor cable to connect to a door switch or another panel but the cable gets routed along a machine frame does it need to be a -ER rating? It's technically exposed outside of a cable tray or conduit. Are there special cable ratings needed for this kind of installation?
Issue 3:
If a cable isn't rated for >300V then it can't be routed next to/with a cable that supplies 480 Volts to a device. Correct?
This could make cable routing on a machine very cumbersome and/or cable selection very costly.
Issues 1: AWM
For the most part, AWM isn't accepted in NFPA 79 for most applications. But I found this:
12.9.2 Appliance wiring material (AWM) shall be permitted under any of the following conditions.
12.9.2(1) Where part of an assembly that has been identified for the indented use
So if a website says their 3 conductor cables with molded ends are intended for sensors and valves are they ok to use? Are there other UL ratings that still need to be met?
Issue 2: Cable routing and rating requirements
If I'm selecting a multi-conductor cable to connect to a door switch or another panel but the cable gets routed along a machine frame does it need to be a -ER rating? It's technically exposed outside of a cable tray or conduit. Are there special cable ratings needed for this kind of installation?
Issue 3:
If a cable isn't rated for >300V then it can't be routed next to/with a cable that supplies 480 Volts to a device. Correct?
This could make cable routing on a machine very cumbersome and/or cable selection very costly.