NFPA 79 compliance

Status
Not open for further replies.

Marco_a

Member
Location
Shreveport, LA
For a cabling on board system, to be in compliance with NFPA 79 requirements, is it mandatory that every single component of the electrical system (sensors, wires, rigid conduits, flexible conduits, cable glands, etc.) has to be UL listed?
 
For a cabling on board system, to be in compliance with NFPA 79 requirements, is it mandatory that every single component of the electrical system (sensors, wires, rigid conduits, flexible conduits, cable glands, etc.) has to be UL listed?
what is an "on board system"?

does NFPA79 even apply?
 
NFPA and UL are not interdependent, so no, technically to meet NFPA 79 requirements, (assuming it is necessary) the components do not need to be UL listed.

However that is a totally separate issue from whether or not the MACHINE must be UL listed. If that is the case, then yes, all components on the machine will need to be either UL listed, or used in a manner UL will approve when the machine is inspected.

If only the control panel must be UL listed and not the entire machine, the components outside of the control panel are not evaluated in the control panel listing, so they would not be an issue. That does not alleviate one from responsible use and installation however.
 
Status
Not open for further replies.
Top