SD Dylan
Member
- Location
- Franklinville, NJ
I have a situation where I am supplying power to a remote I/O enclosure using a multi-conductor control cable, example, and I'd like to utilize the green/yellow conductor as the EGC.
NFPA 79 (2015) 8.2.2.3 states "Equipment grounding conductors and bonding jumpers of the wire type shall not be smaller than shown in Table 8.2.2.3, but shall not be required to be larger than the circuit conductors supplying the equipment."
The smallest size on table 8.2.2.3 is 16AWG. Is the 18AWG green/yellow conductor that is part of the cable allowed to but used as an EGC? The second part "...but shall not be required to be larger than the circuit conductors supplying the equipment." tells me it's ok.
What is your interpretation?
Thanks!