cncsnw

Member
A perennial question in planning an industrial panel with multiple devices, including a variable frequency AC drive for the main spindle motor:

NFPA 79 section 7.2.10.1 says "Each motor controller and its associated wiring shall be protected as an individual branch circuit by a short-circuit
protective device (SCPD) as specified by the controller manufacturer.
The maximum rating of the designated SCPD shall be as shown in Table 7.2.10.1." [which goes on to list the percentage of FLC you may use with various classes of fuse or types of circuit breaker].

For purposes of this requirement, is a VFD a "motor controller"? As such, must it have a dedicated set of branch-rated fuses or UL489 breaker?

In this particular case, the VFD manufacturer specifies a (maximum) 225A MCCB, but I am planning to use a 200A MCCB as the main breaker/disconnect for the panel. I am confident that the VFD, plus the handful of smaller loads on the panel, will not exceed 200A. Besides, the customer only has a 200A service available.

It seems like the 200A main breaker should be sufficient to protect the VFD; yet the above NFPA79 paragraph suggests the drive needs to be "individually" protected.

Any thoughts or experiences on this subject?
 