I am setting up a machine line in usa.
we recieve main power from the city into our main cabinet.
From there we are running a closed nema 4x cableway stainless, around the machine.
according to nec you are only allowed to fill it 20% and you need to correct amp rating of the cables because there are more then 30 conductors.
But i believe that this kind of installation belongs to NFPA79 machine installation.
And in NFPA 79 i can find that cable ratings are the same more then 30 conductors you need to down grade the cable to 35% of its rated value.
But it do not say anything about 20% filling.
there are no cables in the cable ducts that belongs to building installation, only cables that belongs to this internal wiring og the machine line.
So the question is: when 20% filling is not meantioned in NFPA79 is the 20% still valid or do nfpa79 remove the rule from nec. so that we can fill the cable duct more then 20% as long as we correct for heat(downgrade the cables)
Best regards.
Rene Christensen.
Sorry for my bad english is from Sweden.
I am setting up a machine line in usa.
we recieve main power from the city into our main cabinet.
From there we are running a closed nema 4x cableway stainless, around the machine.
according to nec you are only allowed to fill it 20% and you need to correct amp rating of the cables because there are more then 30 conductors.
But i believe that this kind of installation belongs to NFPA79 machine installation.
And in NFPA 79 i can find that cable ratings are the same more then 30 conductors you need to down grade the cable to 35% of its rated value.
But it do not say anything about 20% filling.
there are no cables in the cable ducts that belongs to building installation, only cables that belongs to this internal wiring og the machine line.
So the question is: when 20% filling is not meantioned in NFPA79 is the 20% still valid or do nfpa79 remove the rule from nec. so that we can fill the cable duct more then 20% as long as we correct for heat(downgrade the cables)
Best regards.
Rene Christensen.