W wireday Senior Member Location New England Occupation Master electrician Dec 29, 2016 #1 Could someone reference NFPA 79 where it indicates minimum size LFMC.Thank you
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Dec 29, 2016 #2 wireday said: Could someone reference NFPA 79 where it indicates minimum size LFMC.Thank you Click to expand... 14.5.4.1.1 Flexible metal conduit (FMC) and liquidtight flex- ible metal conduit (LFMC) minimum electrical trade size shall be metric designator 12 (trade size 3⁄8). Exception: Thermocouples and other sensors.
wireday said: Could someone reference NFPA 79 where it indicates minimum size LFMC.Thank you Click to expand... 14.5.4.1.1 Flexible metal conduit (FMC) and liquidtight flex- ible metal conduit (LFMC) minimum electrical trade size shall be metric designator 12 (trade size 3⁄8). Exception: Thermocouples and other sensors.
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Dec 29, 2016 #4 wireday said: Thank you Click to expand... You're welcome.